  • Registered Users Posts: 2,193 ✭✭✭christy c


    How do know if you have a gravity fed system? Says on Amazon that Drayton does not work with it. House is 25 years old


  • Registered Users Posts: 6,493 ✭✭✭deezell


    christy c wrote: »
    How do know if you have a gravity fed system? Says on Amazon that Drayton does not work with it. House is 25 years old

    Not if there are no zone valves and just a pump. However, if the CH zones are on zone valves, and the HW is gravity, then you can bind the zone valve relay outputs to the HW output from the Drayton, the boiler will fire for any of the 2,/3 zones, and gravity heat the HW. You can have HW only if the CH zones are off, but not CH only. If you have 3 zone valves, your HW is not gravity anymore. I explained gravity mode of a 2 zone timer a few posts back, many non smart electronic 2 zone timers have a built in mode switch to change the two outputs from CH zone and HW zone to Boiler call and circulation pump. Drayton two zone box has no mode switch, in hardware or software. Tado ext kit has it in software by a support call Nest uses 2 pole volt free relays, so you can wire the logic yourself as I showed a few posts back. Any 2 zone timer with CH/HW on and off terminals, with an unwired common for each, can be wired thus.


  • Registered Users Posts: 6,493 ✭✭✭deezell


    I should add that you have a gravity HW system if the HW heats without the aid of the circulation pump which supplies the rads.


  • Registered Users Posts: 1,436 ✭✭✭NewClareman


    deezell wrote: »
    Then Drayton Kit 3 is perfect. It's gone back up in price though from that deal earlier. Now £204.

    Hi deezel, Im wondering if I could use 2 x the Drayton 2 kits instead. It would work out much cheaper, as the radiator valves are included. Ive given mote info in the thread I just posted. Is this possible?


  • Moderators, Home & Garden Moderators Posts: 5,775 Mod ✭✭✭✭graememk


    The Tado systems are on sale on amazon for prime day, as expected.


  • Advertisement
  • Registered Users Posts: 1,134 ✭✭✭maxamillius


    deezell wrote: »
    Here it is boiler fires for either HW or CH timed event, but pump only operates for CH.


    528990.png

    Assume this is exactly how Tado works for gravity systems also?


  • Registered Users Posts: 6,493 ✭✭✭deezell


    Hi deezel, Im wondering if I could use 2 x the Drayton 2 kits instead. It would work out much cheaper, as the radiator valves are included. Ive given mote info in the thread I just posted. Is this possible?

    No reason why not, as long as two receivers can be paired to the app, I'd imagine it should work. Its perfectly possible you might have multiple stat zones, more th a 2 stats, so you would need to add 2 kits. The 1 ch zone and the 1 CH+HW kits are £47 and £57, £104. Seems the best way. Those so called 24hr deals can wreck your head though, they appear and disappear in minutes sometimes.


  • Registered Users Posts: 6,493 ✭✭✭deezell


    Assume this is exactly how Tado works for gravity systems also?

    Not as such. Tado ext kit has a mode switch for a single volt free 2 pole relay for CH only, or else two live wired outputs, CH and HW, and normally these are used to open their respective zone valves, going live for their independent timers.
    For a gravity system, you want the HW terminal to go live for either HW or CH timed event, and this terminal is wired directly to fire the boiler. The CH terminal is wired only to the circulation pump, so either HW or CH will heat HW by gravity, but only CH will pump the running boiler to the rads. Tado support can set the ext. kit to operate this way, while you must set it to mode 2, 2 zone output. You can see from the diagram that in this mode, the zone relay commons are hard wired to live, so it's not possible to use that Nest wiring arrangement, but tado support can make it happen in software.
    To that end, you can mimic the gravity mode effect on any 2 zone timer by including CH timing slots on the HW schedule, but that's just a bodge.

    529211.png


  • Registered Users Posts: 2,193 ✭✭✭christy c


    deezell wrote: »
    I should add that you have a gravity HW system if the HW heats without the aid of the circulation pump which supplies the rads.

    Given that I can't heat HW on its own through my boiler, would that mean its not gravity fed?

    Thanks for the info, you're a wealth of information


  • Registered Users Posts: 4,523 ✭✭✭savemejebus


    deezell wrote: »
    Then Drayton Kit 3 is perfect. It's gone back up in price though from that deal earlier. Now £204.

    Keep an eye on this today. The £204 price is not sold by Amazon, if Amazon themselves get more stock in it should be at the discounted price till the end of the day. Also, the multiple zone kit with 1 stat and two smart TRVs is still available and discounted.


  • Advertisement
  • Registered Users Posts: 220 ✭✭Caillte


    graememk wrote: »
    The Tado systems are on sale on amazon for prime day, as expected.

    Yup bought myself 8 more tado TRVs for £30 each to complete the whole house. Sweet!


  • Registered Users Posts: 159 ✭✭captainshamroc


    christy c wrote: »
    How do know if you have a gravity fed system? Says on Amazon that Drayton does not work with it. House is 25 years old

    From Drayton tech support
    If you have no motorised valves on the system it will be gravity, if you have it will be conventional pumped system.

    I had a big discussion with their TS over this. I have a 35 year old house and a a single zone boiler they stopped making in the 90's. The hub basically just fires the on switch for the boiler so why would the Drayton hub not work in a gravity fed system. They would never admit that it would work fine but did admit that the reason that gravity fed were not supported was health & safety not technical.

    From Drayton tech support
    Gravity Fed systems do not comply with part L of the building Legislation. In other words, do not meet the up-to-date building regulation requirements.

    i.e. they are not going to invest in testing something that won't go in a new house and if they haven't tested they are not going to say it works fine. I installed and it works fine.


  • Registered Users Posts: 2,193 ✭✭✭christy c


    From Drayton tech support
    If you have no motorised valves on the system it will be gravity, if you have it will be conventional pumped system.

    I had a big discussion with their TS over this. I have a 35 year old house and a a single zone boiler they stopped making in the 90's. The hub basically just fires the on switch for the boiler so why would the Drayton hub not work in a gravity fed system. They would never admit that it would work fine but did admit that the reason that gravity fed were not supported was health & safety not technical.

    From Drayton tech support
    Gravity Fed systems do not comply with part L of the building Legislation. In other words, do not meet the up-to-date building regulation requirements.

    i.e. they are not going to invest in testing something that won't go in a new house and if they haven't tested they are not going to say it works fine. I installed and it works fine.

    Good to hear. Had pulled the trigger just before you posted!


  • Registered Users Posts: 214 ✭✭dendof


    Didn't want to clog the bargain thread so asking here if possible.
    I currently have Nest installed. Looking to make the switch to Tado while it's Prime Day.
    But I'm unsure should I get wired, or wireless version. I've attached my current setup and also wondering if I go for wired, is it a straight swap


  • Registered Users Posts: 6,493 ✭✭✭deezell


    dendof wrote: »
    Didn't want to clog the bargain thread so asking here if possible.
    I currently have Nest installed. Looking to make the switch to Tado while it's Prime Day.
    But I'm unsure should I get wired, or wireless version. I've attached my current setup and also wondering if I go for wired, is it a straight swap

    It's a straight swap if you go wireless, as currently that's what you have, Nest stat wireless to the heatlink relay, which sends wired SL for CH and HW. A Tado stat with an ext. kit relay will exactly replace this. You can't control HW with just a wired Tado stat.


  • Registered Users Posts: 6,493 ✭✭✭deezell


    christy c wrote: »
    Good to hear. Had pulled the trigger just before you posted!

    You're missing the point slightly. A gravity HW system assumes you might want to heat just HW. The system described above is just a CH system with HW as a consequence of heating the rads, hardly practical in the middle of summer. Any stat will turn a boiler on and off. A 2 zone gravity system gives independent HW by virtue of muting the circulation pump giving HW only when the boiler is fired, and the signal logic for this is not available on the two outputs of a wiser CH/HW controller.


  • Registered Users Posts: 2,193 ✭✭✭christy c


    deezell wrote: »
    You're missing the point slightly. A gravity HW system assumes you might want to heat just HW. The system described above is just a CH system with HW as a consequence of heating the rads, hardly practical in the middle of summer. Any stat will turn a boiler on and off. A 2 zone gravity system gives independent HW by virtue of muting the circulation pump giving HW only when the boiler is fired, and the signal logic for this is not available on the two outputs of a wiser CH/HW controller.

    In the system above, if all the TRVs are off would that would heat water? Although possibly not very efficiently?

    The ability to turn on CH during the winter remotely, adjust room temperature, turn on single radiators is the appeal for me. If I cannot heat water on it's own during summer thats not a deal breaker by any means.

    I have never used my boiler for HW only as it does not have the ability at the moment.


  • Registered Users Posts: 6,493 ✭✭✭deezell


    christy c wrote: »
    In the system above, if all the TRVs are off would that would heat water? Although possibly not very efficiently?

    The ability to turn on CH during the winter remotely, adjust room temperature, turn on single radiators is the appeal for me. If I cannot heat water on it's own during summer thats not a deal breaker by any means.

    I have never used my boiler for HW only as it does not have the ability at the moment.

    Then you never had a gravity HW heating option.That's ok though, as you are installing a full TRV system, and each one is effectively a zone valve. It matters not if your HW heats by gravity or by circulation pump, in your system calling the boiler using the HW output of the Drayton receiver will result in HW only heating, as all TRVs will be closed. In this instance the pump will send all the boiler water through the cylinder coil, so HW will heat up very quickly and efficiently. You will not be using gravity to heat your water. You only have one input to your existing system to fire the boiler, so simply linking the HW on terminal to the CH on terminal, the boiler will fire for either event but TRVs will only open when their schedule calls for an increase in temperature.


  • Registered Users Posts: 2,193 ✭✭✭christy c


    I could be wrong but if the TRVs are closed, the circulation pump won’t run, boiler won’t fire and therefore you won’t be able to heat the hot water. You could only hear the hot water whilst you are heating the rest of the house.

    As I have said, I am far from an expert on this, but would all TRVs closed not be the equivalent of turning off all radiators and turning on the boiler? How would the boiler/pump know?


  • Registered Users Posts: 1,134 ✭✭✭maxamillius


    During the summer I usually leave the stay down and use gravity to heat the water.

    I suppose if you had TRVs in every room and these were off, the rooms wouldn’t heat and the water would thus removing the need for a Tado extension kit?

    Maybe not the correct way to do it but you would still achieve the same result wouldn’t you?

    Basically whenever the boiler is on for a ch timed event, the pump runs, if I have 6 rooms with TRVs and the temperature turned down on them, the rooms don’t heat but the water does.

    Am I on the right track?


  • Advertisement
  • Registered Users Posts: 6,493 ✭✭✭deezell


    christy c wrote: »
    As I have said, I am far from an expert on this, but would all TRVs closed not be the equivalent of turning off all radiators and turning on the boiler? How would the boiler/pump know?
    The stat and reveiver/controller you are buying is the 2 zone device, HW and CH, it will have two live timed output terminals, HW On and CH On. The CH goes live whenever a TRV calls for heat, firing the boiler. The HW one goes live whenever a programmed timed HW event comes on. Simply connecting these two terminals together will ensure the boiler comes on for a HW event even if there are no TRV events, and all TRVs are closed.
    If you buy the single zone kit then you just have a CH timer/stat, no seperate relay to close for the app HW timer, so no way to fire the boiler while all TRVs are closed.


  • Registered Users Posts: 2,193 ✭✭✭christy c


    deezell wrote: »
    The stat and reveiver/controller you are buying is the 2 zone device, HW and CH, it will have two live timed output terminals, HW On and CH On. The CH goes live whenever a TRV calls for heat, firing the boiler. The HW one goes live whenever a programmed timed HW event comes on. Simply connecting these two terminals together will ensure the boiler comes on for a HW event even if there are no TRV events, and all TRVs are closed.
    If you buy the single zone kit then you just have a CH timer/stat, no seperate relay to close for the app HW timer, so no way to fire the boiler while all TRVs are closed.

    Ta, so stick with what i have? Have 46 mins to decide :)


  • Registered Users Posts: 6,493 ✭✭✭deezell


    During the summer I usually leave the stay down and use gravity to heat the water.

    I suppose if you had TRVs in every room and these were off, the rooms wouldn’t heat and the water would thus removing the need for a Tado extension kit?

    Maybe not the correct way to do it but you would still achieve the same result wouldn’t you?

    Basically whenever the boiler is on for a ch timed event, the pump runs, if I have 6 rooms with TRVs and the temperature turned down on them, the rooms don’t heat but the water does.

    Am I on the right track?

    Not really, if the TRVs are turned down they won't call the boiler, so HW can't heat unless at least one TRV is on. The Tado ext kit supplies a seperate relay terminal which responds to a HW timed schedule. No ext kit, no timer schedule, no way to fire the boiler in either pumped or gravity mode for HW only.


  • Registered Users Posts: 6,493 ✭✭✭deezell


    christy c wrote: »
    Ta, so stick with what i have? Have 46 mins to decide :)
    If you mean the stat with HW control option( 2 zone) plus all the extra TRVs, yes, go for it.


  • Registered Users Posts: 1,134 ✭✭✭maxamillius


    deezell wrote: »
    Not really, if the TRVs are turned down they won't call the boiler, so HW can't heat unless at least one TRV is on. The Tado ext kit supplies a seperate relay terminal which responds to a HW timed schedule. No ext kit, no timer schedule, no way to fire the boiler in either pumped or gravity mode for HW only.

    Fair play to you for putting up with the ridiculous amount of questions, a wealth of knowledge you are!


  • Registered Users Posts: 1,134 ✭✭✭maxamillius


    Again this might be a stupid question, if I had Tado with extension kit, let’s say I don’t have timed events setup for the hot water, if I decide at say 7 pm that evening I want to put on the boiler for hot water, do I need to login and setup a timer or is there a way of just turning it on, like a boost button maybe?

    Also presumably if you were to install TRVs in every room, there is no need for the old wall stag in the hallway?


  • Registered Users Posts: 6,493 ✭✭✭deezell


    Again this might be a stupid question, if I had Tado with extension kit, let’s say I don’t have timed events setup for the hot water, if I decide at say 7 pm that evening I want to put on the boiler for hot water, do I need to login and setup a timer or is there a way of just turning it on, like a boost button maybe?

    Also presumably if you were to install TRVs in every room, there is no need for the old wall stag in the hallway?
    No need to log into the app on your phone, just open it and set the HW on. You can link it to Alexa, or Smart Things, or via Google voice, a whole host of ways, " Alexa, heat the water", this will boost for a set period, adjustable in the app. Takes a little setting up, but if you're into it you'll know the ropes. I just have CH on my tado, HW is still on the old system on a timer and stat. I never have to go near it, I just keep the cylinder hot as its well insulated. I can boost the CH by voice, OK Google, or Alexa, or by a programmed IFTTT button on my phone.


  • Registered Users Posts: 159 ✭✭captainshamroc


    deezell wrote: »
    The stat and reveiver/controller you are buying is the 2 zone device, HW and CH, it will have two live timed output terminals, HW On and CH On. The CH goes live whenever a TRV calls for heat, firing the boiler. The HW one goes live whenever a programmed timed HW event comes on. Simply connecting these two terminals together will ensure the boiler comes on for a HW event even if there are no TRV events, and all TRVs are closed.
    If you buy the single zone kit then you just have a CH timer/stat, no seperate relay to close for the app HW timer, so no way to fire the boiler while all TRVs are closed.

    A wealth of knowledge as usual.
    I had never even considered wiring the HW and CH together. I've plenty of HW in the winter but have to use the immersion in the summer. Could be a solution. I have 2 channel Drayton hub in the box somewhere that I was hanging on to incase I changed the plumbing when my old boiler finally dies.


  • Registered Users Posts: 206 ✭✭Skidmcmarx


    I posted this in the Plumbing & Heating forum but I thought it might be a good idea to ask here too. There seems to be a lot of good information being given.

    I've moved into a new to me house recently which had a Climote installed.

    We needed to replace the boiler almost immediately as the old one was on the way out. The boiler was installed successfully and is working away fine with the Climote that was there when we moved in.

    Now that it's done, we want to move over to Nest.

    The Climote is controlling three zones. Downstairs, Hotwater tank & Upstairs

    Attached is the wiring of the climote.
    We have a stat in the living room and a stat on the landing to be replaced by a nest each.

    My question is, based on the wiring seen in the picture, can both nest heat links be places in the same place?


    Any insight would be really appreciated.


  • Advertisement
  • Registered Users Posts: 1,134 ✭✭✭maxamillius


    I’ve drawn it all out now and understand how it’s meant to be wired and setup, my only remaining question is,

    In my old setup I have a wall stat to switch on the pump for ch. if I was to put TRVs in all rooms, I don’t need the wall stat anymore correct?

    In this case I would get the smart radiator kit with the extension, as opposed to the smart thermostat kit? Correct?

    And finally is there a requirement to leave one radiator without trv?

    Edit

    If I decided to just get the smart stat kit, I think this comes with the extension as standard, the wireless stat goes in place of my wall stat and is used to fire Boiler and pump. if I decide to add TRVs at a later date, would I then get rid of the wall stat? Or leave it there in the hall and not put a TRV in the hall radiator?